Furnishing Flammability Guidelines
at the University of Rochester

Background:

The University of Rochester is a medium size university with approximately 8,400 students, 3,500 of which live in campus housing, and a large (2.6 million sq ft) medical center which typically houses 800 patients and employs 8,500 employees. The University Fire Marshal's Office is associated with Environmental Health & Safety and is staffed by a Fire Marshal, a unit secretary, three full time Fire Safety Inspectors, one part time intern from the local community college fire science program, and one part time University student employee who inspects University owned apartments.

This office is responsible for construction plan reviews, testing the flammability of products, fire equipment maintenance, building and construction site inspections, conducting fire drills, providing employee and student training, fire investigation, and the development of university- wide design and construction standards related to fire safety.

The Problem:

About three years ago, the University of Rochester Fire Marshal's Office became involved in a study of the flammability of furnishings following a request to do so by a hospital evaluation committee and a threatening fire involving a fire-resistent mattress. The initial intent was to evaluate the effectiveness of existing standards and vendors claims. The results of our study were quite startling, causing us to create our own fire safety guidelines for furnishings. Since then, our guidelines have been written up in both "Fire Engineering" and "Fireline" magazines, resulting in numerous inquiries from throughout the U.S.

Currently, in my community, there are no local or state enforceable codes which apply to the fire-resistancy of furnishings. All that we have to rely on are national standards, such as the National Institute of Standards and Technology tests which manufacturers use to design fire-resistent furnishings. The problem is that these tests focus primarily on cigarette ignition of the product surface fabric. The style and geometry of the product, in terms of creating pockets where a dropped cigarette or other hot items can come to rest, and the ticking of mattresses and the substrate of furniture, commonly made of polyurethane, are often excluded from the testing process.

Also, a product can meet these standards by having fire-resistancy as an inherent part of the fabric or by having a fire-resistant chemical applied to the surface. This can make a vast difference in long term fire resistancy because of wear and tear and regular cleaning. Chemicals tend to wear off or wash out, resulting in a product that no longer meets requirements. The fire resistant surface fabric can also be violated, exposing the combustible non-resistent substrate. So the question becomes, are these standards enough? The State of California and the City of Boston apparently don't think so. They have their own standards related to furnishings which include a composite burn test as opposed to a component burn test. Other states such as Minnesota, Ohio, and Massachusetts have adopted standards for medical care facilities. Six other states are considering adoption of broader regulations for all upholstered furniture.

We at the University of Rochester don't think the existing national standards are enough either, which is why we developed our own guidelines. Even the National Fire Protection Association, which has general requirements related to ignition from a cigarette in chapter 31 of the Life Safety Code for certain occupancies, doesn't address smoke levels or smoke toxicity.

The rate of burn and heat release, in terms of preventing flashover, are now beginning to receive more attention but smoke density and toxicity are still not considered; and smoke is, as we all know, the primary killer in fires.

The burning of common furnishings such as mattresses and stuffed furniture can release a number of toxic gases such as carbon monoxide, hydrogen cyanide (recent studies in France have discovered that this is as common a cause of death in fires as carbon monoxide), nitrogen dioxide and hydrogen chloride. Human tolerance of these products of combustion is very low, resulting in quick and certain death for occupants.

Interior finishes, like furnishings, also need to be considered. They are required by New York state code to meet certain flame spread ratings based on the type of occupancy but there are no requirements related to smoke levels or toxicity for these products.

This leaves it up to the institution or local authority to determine whether the minimum standards and codes offer an appropriate level of fire safety for furnishings and interior finishes or whether it is better to develop local requirements. Considering that upholstered furniture and bedding are very common points of fire origin in multiple dwellings, resulting in numerous deaths and millions of dollars in damages each year, we felt local requirements were necessary.

As I mentioned earlier, the initial concern over this issue came from our hospital. The Hospital Value Analysis Committee, which is responsible for approving new products for use in the hospital, approached our department with a concern about the use of foam mattresses in several special care units. Then a potentially serious fire occurred in the psychiatric emergency department when a very disturbed patient convinced his family to loosen his restraints and give him a cigarette and lighter which he then used to ignite the mattress on his bed. The resulting fire caused extensive smoke spread throughout a large portion of the emergency department, disrupting services for over an hour.

The problem was magnified locally when the Rochester Fire Department responded to a multi-fatal fire in a residence and the toxic gases from burning furnishings were focused on by the media as the cause of death. Research:

VIDEO - STANDARD FIRE RESISTANT MATTRESS BURN TEST

Our project began with research to establish a good understanding of the problem and to set priorities. The first step was a large scale burn test of foam mattresses which were presented by the Value Analysis Committee.

Four different vendors presented mattresses which allegedly met all current fire safety standards. All suggested that their product would pass our test and each eagerly provided a mattress to burn. All four mattresses were taken to the fire department's training academy and, with the joint involvement of University and fire department personnel, subjected to large-scale testing. Each mattress was placed on a metal bed frame and subjected to non-scientific burn tests consisting of exposure to a lighted cigarette and exposure to a single match, with both placed in the center of the mattress. Several variations of each test were planned, both with and without bed sheets. There was also an intention to subject each mattress to a waste basket fire placed adjacent to the mattress. All mattresses did well with the cigarette test. Three of the four eventually ignited but burned slowly, indicating compliance with national test methods. The fourth mattress did not ignite from the cigarette. The second test, involving a lit match, did not fair as well. One mattress ignited soon after exposure and quickly burned with such intensity that all members of the test team, although prepared to extinguish the fire with fire extinguishers, were forced to evacuate without any chance of extinguishment. Two mattresses also failed because of unacceptable ignition and burn rates when exposed to a waste basket fire. Only one was accepted for use in our hospital.

Another test, using a waste basket fire, was conducted on a dormitory mattress taken from existing stock. This mattress was also judged to be unacceptable because of ignition and burn rates, plus the density of smoke created. A cigarette test of a dormitory mattress resulted in a finding that the substrate smolders internally for a considerable period of time with little or no external signs of fire. This could possibly lead to a lack of recognition of a fire or a false belief that the fire is out. A subsequent test of a dormitory style waste basket was conducted in conjunction with local fire investigators and was found to ignite easily and burn for a total of 32 minutes to the point of breakdown to a flowing liquid and eventually to total consumption. The results of these tests, coupled with the significant smoke from, and burn damage to, the mattress involved in the psychiatric unit fire, proved to us that existing requirements were simply not enough to adequately protect our university community. The development of standards for furnishings at the University became a commitment, beginning with a focus on mattresses. The second phase of our research involved a review of existing codes and standards related to furnishing flammability such as the California Department of Consumer Affairs Standard, the Boston Fire Department Standard, and the NFPA Life Safety Code Standard. We also did extensive research on toxic air contaminants produced by burning furnishings. The Industrial Hygienist unit of EH&S was very helpful in providing materials and interpreting findings of toxicity studies. With the knowledge gained from the large-scale fire tests and from the literature research, we were even more committed to the development of a University flammability standard.

The next step was performing computer modeling of escape times from a typical University of Rochester dormitory to show the length of time needed to control fire and smoke spread until all occupants could escape. We found the average escape time for a typical dormitory student to be just under three minutes but a variety of factors could increase this escape time to almost ten minutes. Based on our fire tests and information from toxicity studies, coupled with projected escape times, it was possible to demonstrate that strict fire and smoke controls for furnishings were needed. This allowed us to gain administrative support for our project. Development:

Development of our guidelines began by contacting our Purchasing Department and our legal people to obtain information necessary to produce an acceptable format which would be non-discriminatory to vendors, would keep product costs at acceptable levels, and would not place the University at an unacceptable level of risk because we implemented more stringent standards. We then identified the necessary elements for our standard and developed the criteria for each element. Many of these criteria were taken from existing standards and modified where necessary to meet our needs. We then contacted several vendors to verify that a product could be manufactured that would meet our guidelines without adding considerable cost. We found that they could.

TEST CRITERIA AND TEST FORM OVERHEADS.

A test criteria for documentation and consistency was then prepared. For large-scale tests, we chose the California Flammability Test Procedure for Mattresses for Use in High Risk Occupancies known as Cal 121. For small scale tests, we chose the NFPA 701 Standard Methods of Fire Tests for Flame-Resistant Textiles and Films such as carpeting, wall coverings, and other interior finishes. From there, we arrived at a decision as to what would constitute acceptance. Our desire was not to prepare rigid standards that limit our flexibility for acceptance. We merely wanted to establish guidelines that would eliminate any item that had the potential to create flashover and untenable smoke conditions prior to rescuing victims and prior to completing an orderly evacuation. We also consulted with the Rochester Fire Department to be certain they were in agreement with our approach and with our guidelines in terms of technical content. They found no problems with either and suggested their use throughout the community.

Once these steps were completed and a full draft of the guidelines was prepared, our purchasing, legal and administrative personnel performed a complete review, making appropriate wording changes without changing the scope of the document. The final step was a review by local fire officials and by peers from area institutions. This step resulted in more minor changes to make the guidelines more global for community use but eventually we were ready for implementation.

"GUIDELINES - FINAL PRODUCT" OVERHEADS (2)

Implementation:

Implementation involved making arrangements for testing on a regular basis, both internally for small scale tests and at the local fire academy for large scale testing. We initially used a fume hood within our office for small scale tests but recently we obtained a glove box which we modified to meet our needs. By using the fume hood, we were able to observe smoke conditions but the fume hood did not provide the ability to test smoke density or to obtain toxic gas readings. With the glove box, we are able to capture the products of combustion for testing. Once test arrangements were in place and an appropriate form was developed to report our findings, members of the University community responsible for specifying, ordering, or installing any furnishings or interior finishes were notified of the guidelines in writing, advising them to contact our office before using an item to assure their product was in compliance. Because we were interested in all forms of furnishings, we also suggested that we be allowed to look at product design to check for vulnerable ignition points and wear points, and to look for pockets where ignition materials could become trapped.

Most everyone we communicated with understood the reasoning behind the guidelines and complied. A few were resistent, believing that existing standards were sufficient and citing the old adage "nothing serious has happened in thirty years so why should we worry about it now". We responded that we prefer to be pro- active as opposed to reactive. We don't want to wait until a fire causes a death to act.

Review:

In the time that our guidelines have been in place, we have experienced good cooperation from most all interested parties at the University. Numerous products have been submitted for testing with mixed results. Many perform as advertised but a significant number have failed to meet advertized compliance standards or failed to comply with our guidelines, and therefore have been rejected for use at our University.

PICU VIDEO.

Because of the guideline designation as opposed to required standards, we are allowed flexibility in judging acceptability. We can look at the results of the product test, evaluate the type of use for which the product is intended and make an informed decision on allowing use. In addition, the entire University community is more aware of fire safety concerns because of these guidelines.

Our Facilities people ask about the acceptability of new products they intend to use such as pipe coverings, our Purchasing Department contacts us to check on the status of new furniture and furnishing products, our Design & Construction people keep us in the loop on products they intend to use in construction and renovation projects, and employees call to ask about the use of certain furnishings because they have been made aware of the guidelines. Various University committees also contact us as part of their evaluation process to receive information on design and fire resistancy on products being considered for use.

Overall we are pleased with the outcome of our furnishing flammability guideline project and feel that fire safety at the University of Rochester has been enhanced because of them.

csaoutln.172 7-21-93